How to fix Error 80A3 Modbus TCP MB_client ?

Hi Everyone!

I use a s7-1500 controller. I use MB_CLIENT function to read data from an other PLC. Everything work fine until I make change in my project and download to the PLC. I have error 80A3 and impossible to acknowledge until I make a stop/Run of the plc.

Anyone can help me?

Best Regards,

0
0
Like1 User
1 User

Related Questions

4 Answers

  1. Hi,

    In my case, I used multiple MB_client function blocks to read data. I was using the same client ID for all of them. I changed the connection ID of those differents connections and the problem was fixed.

    if you have 3 instances of MB_client. you must set unique connection ID per instance

    Example:

    ID = 1  for MB_client_1 instance

    ID = 2  for MB_client_2 instance

    ID = 3  for MB_client_3 instance

    Regards

  2. Hi Maesa,

    If you use instances declared in a FB function.

    Try to use a global instance of MB_clien like this:

    use a global DB to declare the “ModbusDataconnectParamClient” structure.

    This will fix your problem and when you download the project, it will not cause problem for MB_client function.

    hope this will help you